if any knows that plz tell me about that because there is ID fan of boiler his panel of star delta

and it stopped and restart atonce

that's problem for the motor that's why

if u know about that then plz tell me

ok thanks

 
  Answered by     K. NARAYAN, None, None  | 03 12 2010 04:06:57 +0000
[ Delete ]
[ Edit ]
Not Rated

Most temperature controllers have quite a few parameters which can be set by the user.

One such parameter is the Deadband.

If the temperature set point is 125 degrees , as in your case , then once the controller switches off its output ( when the actual temperature has exceeded the setpoint ) , then the controller output will come on again when the actual temperature has gone below the ( setpoint - deadband ). If the deadband in your controller is 3 degrees , then certainly the controller output will come on again when the temperature falls below 122 degrees.

Another set of parameters are the P , I and D values. Depending on these values , the controller output may go off before the setpoint is reached , so as to minimize overshoot.

Some of the more sophisticated controllers have what is called AUTOTUNE. When this is made on , the controller tunes itself to the process , so as to identify the appropriate values of P , I and D.

If you give the model number of your controller , probably we can get more information from the Internet.

  Answered by     ravi gupta, instrumentation & control engg., Rishraj filaments ltd  | 03 11 2010 15:57:26 +0000
[ Delete ]
[ Edit ]
Not Rated

If that proportional value of temp. controller is greater than its set value then definitely it neglet the set point value
ok 
Which temp controller u r using?
can u give some report about that ok
bye take care

tell me soon

  Answered by     surinder gupta, working as GM, pee vee textiles limited  | 03 11 2010 13:34:51 +0000
[ Delete ]
[ Edit ]
Not Rated

for controlling speed of Id fan motor we can put vfd in motre , itwill mentain the speed as per require and will avoid frequent on off ,of the motor.

  Answered by     surinder gupta, working as GM, pee vee textiles limited  | 03 11 2010 13:34:36 +0000
[ Delete ]
[ Edit ]
Not Rated

for controlling speed of Id fan motor we can put vfd in motre , itwill mentain the speed as per require and will avoid frequent on off ,of the motor.

  Answered by     surinder gupta, working as GM, pee vee textiles limited  | 03 11 2010 13:33:47 +0000
[ Delete ]
[ Edit ]
Not Rated

for controlling speed of Id fan motor we can put vfd in motre , itwill mentain the speed as per require and will avoid frequent on off ,of the motor.

 
Leading Recruitment Firm
  • Create a confidential Career Profile and Resume/C.V. online
  • Get advice for planning their career and for marketing of experience and skills
  • Maximize awareness of and access to the best career opportunities
Viewers also viewed
The progress what India makes is not reaching to grass roots.After 62 years of independence we...
 
7 referals 5 arguments, 646 views
 
2135 referals 6 votes, 215 views
India has a very vast diversity...and in a country like India..Is it important for us all to...
 
653 referals 12 arguments, 77 views
more...  
Unanswered Questions (126)
  HI all, I am presently conducting an online survey for IT/Software professionals in India as a...
 
0 referals 0 answers, 0 views
What is Service Value Agreement? how its going to benefits clients and whats vendors take on it?...
 
0 referals 1 answers, 8 views
If you got the opportunity to become a CM of any one of the state which is in India than what...
 
0 referals 2 answers, 18 views
More From Author
IF ANYBODY KNOWS ABOUT THAT PLZ TELL ME ABOUT THAT BECOZ I M SUFFERING FROM A VERY BAD CONDITION DUE TO THIS OK TELL ME SOON GOD BLESS YOU FOR THIS BYE TAKECARE
If that proportional value of temp. controller is greater than its set value then definitely it neglet the set point value ok  Which temp controller u r using? can u give some report about that ok bye take care tell me soon
Is it possible that temp controller after acheiving his set value like:- 125(set parameter) restart after when it temperature becomes 122?
more...